[labnetwork] Cleanroom cleaning
Kuhn, Jeffrey G
kuhn1 at purdue.edu
Wed Jan 8 07:34:33 EST 2014
Rick,
The cleanroom at Birck is a bay-chase design with a central hallway. The bays are cleaned weekly using a microfiber mop system and UPW as the solvent. The chases are cleaned every two weeks using the same system plus hand cleaning of piping, etc. using cleanroom wipes. 90/10 UPW & IPA is used to spot clean more stubborn contamination as needed. The central hallway floor is cleaned daily (M-F) using the microfiber mops. The wipes are disposable, but the microfiber mops are laundered off-site.
The mop system I mentioned replaced a three step method we formerly used. The old procedure involved using a HEPA vac, followed by a wiper/paddle system with 90/10 UPW & IPA as the solvent, followed by a second HEPA vacuuming. Both methods were approximately equal in their removal of contamination, but the microfiber system is faster since it involves only one step. That allowed us to reduce cleaning personnel by 1/3, which offset the increased cost of the microfiber mop system.
Let me know if you would like more specific information on the mop system or the 3-step system and I'll send it to you.
Regards,
Jeff Kuhn
Facility Engineer
Birck Nanotechnology Center
Purdue University
1205 W. State St.
West Lafayette, IN 47907
Ph: (765) 496-8329
Fax: (765) 496-2018
From: labnetwork-bounces at mtl.mit.edu [mailto:labnetwork-bounces at mtl.mit.edu] On Behalf Of Morrison, Richard H., Jr.
Sent: Monday, January 06, 2014 2:49 PM
To: labnetwork at mtl.mit.edu
Subject: [labnetwork] Cleanroom cleaning
Hi Folks,
Wondering if anybody as a recommended clean routine for a Class 10 cleanroom?
Rick
Draper Laboratory
Group Leader Microfabrication Operations
555 Technology Square
Cambridge Ma, 02139-3563
www.draper.com<http://www.draper.com>
rmorrison at draper.com<mailto:rmorrison at draper.com>
W 617-258-3420
C 508-930-3461
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20140108/e09b661a/attachment.html>
More information about the labnetwork
mailing list