[labnetwork] Thermal load in cleanrooms ISO 5/6
Loïk GENCE
Loik.gence at cetuc.puc-rio.br
Mon Mar 16 15:04:01 EDT 2015
Thank you all for your messages. It helps!
I'll introduced ligthning and FF units in the thermal load calculation.
I can see that the /a priori/ estimation of the diversity factor seems
to be difficult.
Overestimating the thermal load is comfortable, but, here, I really
have to minimize the cost of the HVAC system choosing a proper
size/power of the HVAC because of our limited budget...
Thanks again!
Loïk.
On 16/03/2015 12:55, Mike Young wrote:
> Hi, Loïk. Welcome to the group.
>
> I would caution you about neglecting the heat contribution of the
> cleanroom lighting and the fan filter units. Make sure they are
> really, truly, negligible, because it is not difficult for them to
> dominate the total cleanroom heat load under some conditions! In
> addition, we find that almost all of our equipment is in operation
> almost all of the time, so before you use the .75 diversity factor,
> make sure it is realistic.
>
> The ACS has to be designed to meet the worst-case heat load, which
> will be worst-case weather conditions, plus everything turned on and
> running, plus maximum personnel heat load, under conditions of
> worst-case (maximum) makeup air flow. Getting all of this right is one
> of the most challenging problems in cleanroom design.
>
> Good luck!
>
> --Mike
>
>
>> On Mar 16, 2015, at 10:36 AM, Loïk GENCE <Loik.gence at cetuc.puc-rio.br
>> <mailto:Loik.gence at cetuc.puc-rio.br>> wrote:
>>
>> Hi Everyone,
>>
>> I am working on the design of a small cleanroom facility (70m2) ISO
>> 5/6. Right now, I am dealing with the problem of thermal load,
>> Which is crucial here in Rio, where the average outside temperature
>> is of 30 deg C with a relative humidity of 75-80 %.
>>
>> I would like to have your help and/or comments on several points:
>>
>> Most of the manufacturers do not provide a value for the thermal load
>> (why?). Assuming 2 or max 3 people working simultaneously in the
>> cleanrooms, and usual cleanroom value: 22 deg C - 55% humidity. The
>> main issue is: how can I estimate the cooling power required for the
>> Air Conditioning System (ACS)?
>>
>> I have the list of equipments we'll have and the corresponding
>> electrical power. I assumed the heat generated by 2 users and added
>> the total electrical power dissipated as heat inside of the
>> cleanroom, using a simultaneity factor of 0.75 (all equipments won't
>> be turned on at the same time) and neglected the heat produced by the
>> filter fan and lightning.
>> ***
>> ** - Is it reasonable for dimensioning the ACS cooling power ? *
>>
>> Also most of the equipments have a cooling water circuit. But the
>> cooling power needed is well described in the installation manual
>> provided with the equipments.
>>
>> * - Should I subtract from the **ACS cooling power**value,
>> **the cooling po**wer **from the chillers?*
>>
>> - *Do you think a central and unique chiller (placed outside
>> of the building) is preferred to several smaller chillers placed
>> closer to the equipment?*
>>
>>
>> I thank you very much for your kind help or comments.
>>
>>
>> regards,
>>
>> Loïk.
>>
>> --
>> __________________________________________
>> Dr. Loïk Gence
>>
>> PUC-RIO/CETUC-LABSEM
>>
>> End Rua Marques de São Vicente, 225-Gavea
>> CEP:22451-900 Rio de Janeiro, RJ-Brasil
>>
>> (Telefone) +55 (021) 3527-2193
>>
>> (Mobile) +55 (021) 99156-5558
>>
>> loik.gence at cetuc.puc-rio.br
>> __________________________________________
>> _______________________________________________
>> labnetwork mailing list
>> labnetwork at mtl.mit.edu <mailto:labnetwork at mtl.mit.edu>
>> https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
>
> --
> Michael P. Young (574) 631-3268 (office)
> Nanofabrication Specialist (574) 631-4393 (fax)
> Department of Electrical Engineering (765) 637-6302 (cell)
> University of Notre Dame mike.young at nd.edu <mailto:mike.young at nd.edu>
> B-38 Stinson-Remick Hall
> Notre Dame, IN 46556-5637
>
--
__________________________________________
Dr. Loïk Gence
LABSEM – PUC-RIO
End Rua Marques de São Vicente, 225-Gávea
CEP:22451-900 – Rio de Janeiro, RJ-Brasil
(Telefone) +55 (021) 3527-2193
(Mobile) +55 (021) 99156 5558
loik.gence at cetuc.puc-rio.br
__________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20150316/d40d0044/attachment.html>
More information about the labnetwork
mailing list