[labnetwork] Exhaust of corrosive chemical storage cabinets
Rizik Michael
rmichael at iesengineering.net
Tue Nov 22 11:20:29 EST 2016
I agree with Bill. In California exhausting chemical storage cabinets is not
required by the California Fire code. We are only required to meet minimum
ventilation requirements for the Hazardous Occupancy storage bunker where
such cabinets are stored. This is usually a minimum 1-cfm per square foot.
Regards
Rizik Michael, PE
Principal
Integrated Engineering Services
Office: 408-261-3500
Cell: 408-718-0927
From: labnetwork-bounces at mtl.mit.edu [mailto:labnetwork-bounces at mtl.mit.edu]
On Behalf Of Bill Flounders
Sent: Monday, November 21, 2016 2:03 PM
To: Peter J Duda III; James Marsh; labnetwork at mtl.mit.edu
Cc: James Marsh (mail.mil)
Subject: Re: [labnetwork] Exhaust of corrosive chemical storage cabinets
Jim, Peter,
The TGO Synopsis from South Bay Pipe is a useful guide for many
in this community. Thank you for providing the on line link for all.
However,
I do not consider using the TGO and its description of requirements for
toxic
gases and gas cabinets (chemicals in use) the best reference for evaluating
ventilation requirements for chemical storage cabinets.
I suspect you are evaluating ventilation from chemical storage cabinets
used to store your closed containers of liquid chemicals and whether
this effluent must go through a building scrubber or can be exhausted
directly - or in other cases is not required to be exhausted. My dated
recall is the mechanical and fire code had specific requirements for the
overall room ventilation but not requirements for cabinet ventilation.
Your local Authority Having Jurisdiction (AHJ, most commonly
your local or campus fire marshal) will make the call but I expect you can
obtain guidance on this situation by comparing your storage cabinets to
the situation at your shipping and receiving or EH&S waste handling
facility.
I expect the requirements for storage cabinets of closed (not in use)
containers
to be far more modest than the requirement for a chemical fume hood or other
process equipment that is used to handle open chemical containers.
Re pros and cons instead of discussing code requirements - we have both.
Our chemical inventory room which meets specific overall room ventilation
requirements, has sealed bottles from the manufacturer, and chemical
cabinets that don't stink when you open them - has chem cabinets that are
not
separately ventilated. This saved money and reserved exhaust capacity for
higher priority needs.
When we have a stinky cabinet in the main lab with half filled photoresist
and
waste solvent bottles - even though this is storage - and the room meets
overall
ventilation requirements - and the cabinet is not required to be exhausted -
we added
ventilation to the cabinet and insure we met all 1/2 IDLH exhaust
requirements.
Bill Flounders
UC Berkeley
Peter J Duda III wrote:
Jim
Santa Clara developed what is now known as the Toxic Gas Ordinance way back
in 1988 as a response to the growing number of semiconductor facilities in
that area. It has since been modified and is mostly used as the model for
the Universal Fire Code. While no source is definitive and local codes vary
I have found this document:
<http://www.sbaypipe.org/assets/pdf/TGO_Toxic_Brochure_single%20pages_0519.p
df>
http://www.sbaypipe.org/assets/pdf/TGO_Toxic_Brochure_single%20pages_0519.pd
f
to be extremely helpful in providing general guidance regarding most
standard semiconductor gases. Not only does it cover generally where TGO
varies from the model fire code - There are a lot of good definitions, the
general requirements are very easy to follow and the table of gases provides
easy access to classifications and IDLH, etc. Again one needs to cross
check against your local requirements, but a 20 minute read can give you an
abundance of info regarding what is required throughout much of the US.
Specifically to your question you can see under the general requirements
in the Exhaust Ventilation System which class of gasses are required to be
treated to ½ IDLH. Under the TGO Synopsis you can see under bullet
S what is involved in a treatment system. I leave it to you to
interpret those for your specific application and again to cross check
those requirements against local codes.
Thanks
Peter J Duda
Technical Director, Pritzker Nanofabrication Facility
Institute for Molecular Engineering
University of Chicago
5640 South Ellis Avenue
ERC LL178
Chicago, IL 60637
Office: 773-702-8903
Pager/Text: 773-652-0480
duda at uchicago.edu
ime.uchicago.edu
From: labnetwork-bounces at mtl.mit.edu [mailto:labnetwork-bounces at mtl.mit.edu]
On Behalf Of James Marsh
Sent: Monday, November 21, 2016 10:15 AM
To: labnetwork at mtl.mit.edu
Cc: James Marsh (mail.mil) <mailto:James.e.marsh14.ctr at mail.mil>
<James.e.marsh14.ctr at mail.mil>
Subject: [labnetwork] Exhaust of corrosive chemical storage cabinets
Hello,
I would like some feedback regarding the pros/cons of venting corrosive
chemical storage cabinets to outdoors. I may be looking at the wrong
resources, but after checking NFPA, SEMI, FM Global, both state and
international fire and mechanical codes, I have found only sketchy guidance.
I would welcome either ideas or suggestions of where to look for definitive
guidance.
Thanks, and have a great day.
Jim
James Jim Marsh, Contractor
Facility Manager/Test Coordinator
EOIR Technologies, Inc. A Polaris Company
Supporting
US Army Night Vision and Electronic Sensors Directorate
Semiconductor Material and Fabrication Research Center
10221 Burbeck Rd.
Ft. Belvoir, VA 22060
Ph: (703) 704-1778
Mobile: (703) 498-1279
_______________________________________________
labnetwork mailing list
labnetwork at mtl.mit.edu
https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20161122/a688e017/attachment.html>
More information about the labnetwork
mailing list