Thanks Dan,

Just to be clear we use the steam from the boilers to generate steam for humidity control in a steam to steam humidifier, but you are right the boilers use a lot of water.

Rick


From: Maxwell, Dan [mailto:DMaxwell at hallam-ics.com]
Sent: Wednesday, July 03, 2019 4:19 PM
To: Morrison, Richard H., Jr <rmorrison at draper.com>; labnetwork at mtl.mit.edu
Subject: RE: Steam boiler question

Rick:

I have run your question by our Director of Engineering.

Re-tubing boilers is common. Properly done, the boiler's life is extended, not shortened. We are fans of retubing, especially on a relatively young boiler.

How long should a boiler last?  It depends greatly.  A boiler should last 20 or more years, if water treatment is done properly (remove oxygen down to single digit part-per-billion range, soften/polish the hardness out, maintain an appropriate concentration of corrosion inhibitors).

You mentioned that this boiler supplies humidification loads, which means 100% makeup water (process and heating boilers have return condensate, their makeup rates are much lower, 10-20% makeup). 100% makeup needs excellent water treatment to prevent corrosion in the boiler (which causes the tube leak). If you can't implement good treatment, you will be back in 7 years replacing tubes. With good treatment, it can go 20 years.

One issue some facilities have with humidity-producing boilers is a desire to avoid using corrosion inhibitors as they are concerned they could be deleterious to human health when added to air. When running with no corrosion inhibitors and a carbon steel boiler, a boiler will not last long at all.

Thanks,

Dan Maxwell
Sr. Project Manager
[Hallam-ICS Employee Owned]
dmaxwell at hallam-ICS.com<mailto:dmaxwell at hallam-ics.com>
38 Eastwood Dr, Suite 200
South Burlington, VT 05403
ph. - 802.658.4891
fax. - 802.658.1457
www.Hallam-ICS.com  I  The Hallam-ICS Blog<https://www.hallam-ics.com/blog>

From: labnetwork-bounces at mtl.mit.edu<mailto:labnetwork-bounces at mtl.mit.edu> <labnetwork-bounces at mtl.mit.edu<mailto:labnetwork-bounces at mtl.mit.edu>> On Behalf Of Morrison, Richard H., Jr
Sent: Wednesday, July 3, 2019 9:38 AM
To: labnetwork at mtl.mit.edu<mailto:labnetwork at mtl.mit.edu>
Subject: [labnetwork] Steam boiler question

HI Everyone,

I have a facility question, we have 2 steam boilers which provide heat and steam to make humidity. One boiler has tubes that have leaked and we can either re-tube the boiler (7 years old) or purchase a new boiler. What is the collective wisdom out there around the risk of lifetime of a re-tubed boiler?

Thanks and Happy 4th

Rick



Richard H. Morrison
Principal Member of the Technical Staff
Draper
555 Technology Square
Cambridge, MA
02139-3573

Work  617-258-3420
Cell  508-930-3461
www.draper.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.draper.com&d=DwMFAg&c=O-BWW9H93kQVFMAc6QfJVxm9eRLMg-yhcvRQXl_QHKE&r=oftFKxzO0dBCbGyxZO_aMKUGNGTRaUafWDv8i-rpJxs&m=zCHXalAZhF_l8pNF-yQ8Nyjc8-d_wwz1aIyUYsH2Y9g&s=Te6u49Q2rOkOcAQTjjFjLhIjZH0YjwAtWsPZDpriFLI&e=>

________________________________
Notice: This email and any attachments may contain proprietary (Draper non-public) and/or export-controlled information of Draper. If you are not the intended recipient of this email, please immediately notify the sender by replying to this email and immediately destroy all copies of this email.
________________________________

________________________________


CONFIDENTIALITY NOTICE:
The information contained in this transmission, as well as any accompanying documents, constitutes confidential and/or legally privileged information which is the property of Hallam-ICS. The information is intended solely for the individual entity named on this transmittal sheet. If you are not the designated recipient, you are hereby notified that any disclosure, copying, distribution or taking any action in reliance on this information is strictly prohibited. If you received this in error, please contact the sender and delete the material from any computer. Opinions, conclusions and the information in this message that do not relate to the official business of my firm shall be understood as neither given nor endorsed by it.
________________________________
Notice: This email and any attachments may contain proprietary (Draper non-public) and/or export-controlled information of Draper. If you are not the intended recipient of this email, please immediately notify the sender by replying to this email and immediately destroy all copies of this email.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20190708/516b6598/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3069 bytes
Desc: image001.jpg
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20190708/516b6598/attachment.jpg>


More information about the labnetwork mailing list