[labnetwork] Cl2, BCl3 and Silane sensors for toxic gas monitoring
Kyle Keenan
kckeenan at seas.upenn.edu
Fri Jan 13 16:09:32 EST 2023
Hi Aju,
We have them in the following areas:
- ambient bay
- ambient chase
- gas cabinets
- exhaust ducts for gas boxes/pods
Best,
Kyle
On Fri, Jan 13, 2023 at 4:06 PM Aju Jugessur <Aju.Jugessur at colorado.edu>
wrote:
> Hi all,
>
>
>
> We have ICP etcher and PECVD that use toxic gases such as Cl2, BCl3 and
> Silane. The exhausts from the pumps are connected to a scrubber and ph
> neutralization/acid waste system.
>
>
>
> I am reaching out to get some advice on the specific locations of the
> Honeywell Midas sensors that we use, to detect any gas leak at the etchers
> and toxic gas monitoring system. We have sensors at the gas cabinets and
> ambient sensors at the tools.
>
> However, there seems to be a disagreement between our design team and our
> EHS unit. The design team recommends having the sensors in the gas pods,
> where the leaks are most likely to occur. EHS would like to have the
> ambient sensors at the tools, in the breathing zone areas. As per local
> code requirements, sensors in the gas pods satisfies the safety
> requirements.
>
>
>
> I would like to know what your set-up of the sensor locations for similar
> instruments is that you may have in your facility.
>
> Any insights based on experience will be super helpful.
>
>
>
> Thanks so much,
>
> Aju
>
>
>
>
>
> Aju Jugessur Ph.D. IEEE Sr. Member
>
> Director, Colorado Shared Instrumentation
>
> in Nanofabrication and Characterization (COSINC) Facility
>
> Member of Inclusive Culture Council (ICC)
>
> *University of Colorado Boulder | **College of Engineering & Applied
> Science*
>
> 4001 Discovery Drive, N360G SEEC *|* Boulder, CO 80303*|* *P:*
> 303.735.5019
>
> E-mail: aju.jugessur at colorado.edu
>
> Personal Zoom link: https://cuboulder.zoom.us/my/*ajugessur*
> <https://cuboulder.zoom.us/my/ajugessur>
>
> www.colorado.edu/facility/cosinc
> <https://urldefense.com/v3/__http://www.colorado.edu/facility/cosinc__;!!IBzWLUs!Wr1EO5-PRuEefCfU7Hif4nj9KU4u0oH8jZYzz8W1tsAn8yob4Y7JmbfDX7D25Idw9NfvfQnWb_zCr3ZU5OA_jNg22W6VcT4$>
>
> (MBA candidate, CU, Class of 2023)
>
>
>
> [image: signature_804197951]
>
>
>
>
> *Signature-Strengths: Focus, Activator, Futuristic, Strategic, Achiever
> (CliftonStrengths)*
>
>
>
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
>
> https://urldefense.com/v3/__https://mtl.mit.edu/mailman/listinfo.cgi/labnetwork__;!!IBzWLUs!Wr1EO5-PRuEefCfU7Hif4nj9KU4u0oH8jZYzz8W1tsAn8yob4Y7JmbfDX7D25Idw9NfvfQnWb_zCr3ZU5OA_jNg2DgaKAmM$
>
--
Kyle Keenan
Senior Manager - Laboratory Operations
Quattrone Nanofabrication Facility
University of Pennsylvania
P: 215-898-7560
F: 215-573-4925
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20230113/26e14a20/attachment.html>