[labnetwork] gas room means of egress

Weaver, John R jrweaver at purdue.edu
Mon Nov 5 16:21:03 EST 2012


Always two! If you have a person working in the room and the incident happens between the person and the only exit, he/she is toast! I have doors at each end of my room so that no matter where the incident would occur there is a clear exit path from the room.

John R. Weaver
Facility Manager
Birck Nanotechnology Center
Purdue University
(765) 494-5494
jrweaver at purdue.edu


-----Original Message-----
From: labnetwork-bounces at mtl.mit.edu [mailto:labnetwork-bounces at mtl.mit.edu] On Behalf Of Iulian Codreanu
Sent: Monday, November 05, 2012 11:33 AM
To: Fab Network
Subject: [labnetwork] gas room means of egress

Dear Colleagues,

I am trying to influence a decision on a second means of egress from the gas room at the University of Delaware and your input is very much appreciated.

This is the room where the cabinets for toxic, flammable, and pyrophoric as well as some panels for inert gases will be located.  The room is adjacent to and separated from the cleanroom by a fire rated wall (I was told it is at least two hours-rated).  The code consultant states that a second means of egress is not needed for this H2 occupancy room but I feel it is a must.

How many doors does your gas room have?

Thank you very much.

Iulian
--
iulian Codreanu, Ph.D.
Director of Operations, UD Nanofab
University of Delaware