Iulian,
we have a single egress door from our flammable gas storage room, but there
are two doors from our toxic gas room. One to the outside of the building,
and one to the inside. Their proximity to each other (about 2 feet) though
doesn't really meet with the egress layout you had in mind though. I'm
guessing you're thinking about opposite ends of the storage locations.
Dennis
734.647.2055 Ofc
On Mon, Nov 5, 2012 at 11:32 AM, Iulian Codreanu <codreanu at udel.edu> wrote:
> Dear Colleagues,
>
> I am trying to influence a decision on a second means of egress from the
> gas room at the University of Delaware and your input is very much
> appreciated.
>
> This is the room where the cabinets for toxic, flammable, and pyrophoric
> as well as some panels for inert gases will be located. The room is
> adjacent to and separated from the cleanroom by a fire rated wall (I was
> told it is at least two hours-rated). The code consultant states that a
> second means of egress is not needed for this H2 occupancy room but I feel
> it is a must.
>
> How many doors does your gas room have?
>
> Thank you very much.
>
> Iulian
> --
> iulian Codreanu, Ph.D.
> Director of Operations, UD Nanofab
> University of Delaware
>
> ______________________________**_________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
> https://www-mtl.mit.edu/**mailman/listinfo.cgi/**labnetwork<https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20121105/f47bdf0f/attachment.html>
More information about the labnetwork
mailing list