[labnetwork] Shared Chiller [for equipment cooling] Issues

Kamal Yadav kamal.yadav at gmail.com
Tue Sep 23 01:32:14 EDT 2014


Dear All,

Thank you very much for sharing your experiences.

There is a design where one puts an expansion tank on the return line for
these shared chiller, probably to avoid ripples, flow shocks, that one gets
when another tool is being switched ON or OFF. I found a document which is
attached which talks about designing such cooling water circuits. This
water is only for process equipment cooling, and not facilities equipment
cooling.

If anybody has worked without these expansion tanks, and if using flow
settlers is enough that would be great to know, we may need to modify our
circuits little bit, if needed.

Thanks,
Kamal.




On Mon, Sep 22, 2014 at 8:37 PM, Bob Hamilton <roberthamilton at berkeley.edu>
wrote:

>  Kamal Yadav,
>
> It is difficult to diagnose your issue given the information in your
> e-mail. It is possible a single tool is using more water than it needs and
> therefore reducing the available volume to tools with higher impedance
> cooling circuits. You may also have a blocked cooling channel in a tool(s).
> Consider running water through them, backwards and into an open drain or
> bucket to back-flush them.
>
> A question; what purpose does this chiller serve? Does it supply deionized
> for rf cooling circuits where the resistivity of the water is important or
> does it simply provide equipment cooling? Is it a heat exchanger (HX) or is
> it Freon-based centrifigal chiller? Do you have a rotameter in the cooling
> loop?
>
> Assuming the conductance of various tools allows most of the process
> cooling water to flow through those tools with lowest impedance consider
> adding "flow-setters" to your tools or just to the tool using too much
> water. There are dynamic version of flow-setters that adjust flow to a
> specific volume of liters-per-minute and maintain this constant flow over a
> range of pressure.
>
> At the Marvell NanoLab we've used flow-setters made of brass, PVC and
> stainless depending on the application. If you choose PVC versions, I'd
> pick male pipe thread (mpt) over female pipe thread (fpt). We try and avoid
> threading metal mpt fittings into plastic fpt fittings because the plastic
> fitting may crack at some part of its service life causing flooding.
>
> Appended are a few US links that provide an example of the device I am
> referring to. I've also seen them on EBAY.
> http://www.deanbennett.com/dole-flow-control-valves.htm
> http://www.haysfluidcontrols.ca/hays_automatic_flow_controls_2305.htm
> http://www.merrillmfg.com/product/08-WellPoints/Merrill-Valves/features.php
> http://www.plastomatic.com/fc.html
> http://www.swtwater.com/catalog/1318_flow_controls.htm
>
> Regards from the MNL,
> Bob Hamilton
>
> --
> Robert Hamilton
> University of California at Berkeley
> Marvell NanoLab
> Equipment Eng. Mgr.
> Room 520 Sutardja Dai Hall
> Berkeley, CA 94720-1754bob at eecs.berkeley.edu
> e-mail preferred
> My personal mobile: 510-325-7557
>
>
> On 9/21/2014 11:22 PM, Kamal Yadav wrote:
>
> Dear All,
>
>  We are facing chiller [for cooling water for equipment] issues, most
> likely flow issues, probably due to using same chiller for multiple
> equipment. Though chiller total cooling capacity is able to provide
> flow/pressure but in an shared equipment scenario, could there be issues.
> Suddenly some equipment, in use, trips, because of low flow of cooling
> water probably.
>
>  Did anybody faced these issues, are we diagnosing it correctly?
>
>  Thanks a lot.
>
>  --
>  Thanks,
>  Kamal Yadav
> Sr. Process Technologist
>  IITBNF, EE Department, Annexe,
> IIT Bombay, Powai
> Mumbai 400076
> Internal: 4435
> Cell: 7506144798
> Email: kamal.yadav at gmail.com, kamalyadav at ee.iitb.ac.in
>
>
> _______________________________________________
> labnetwork mailing listlabnetwork at mtl.mit.eduhttps://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
>
>
> --
> Robert Hamilton
> University of California at Berkeley
> Marvell NanoLab
> Equipment Eng. Mgr.
> Room 520 Sutardja Dai Hall
> Berkeley, CA 94720-1754bob at eecs.berkeley.edu
> Phone: 510-809-8600
> Mobile: 510-325-7557 (Emergencies only poor cell phone service in lab)e-mail preferred
>
>
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
> https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
>
>


-- 
Thanks,
Kamal Yadav
Sr. Process Technologist
IITBNF, EE Department, Annexe,
IIT Bombay, Powai
Mumbai 400076
Internal: 4435
Cell: 7506144798
Email: kamal.yadav at gmail.com, kamalyadav at ee.iitb.ac.in
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20140923/84080982/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PCW_Circuit_York_piping0001.pdf
Type: application/pdf
Size: 3676045 bytes
Desc: not available
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20140923/84080982/attachment.pdf>


More information about the labnetwork mailing list