[labnetwork] Temperature specification for facility process chilled water

Dennis Schweiger schweig at umich.edu
Tue Sep 15 05:39:40 EDT 2015


Iain,

one thing I forgot to mention, both of our systems are fabricated from CPVC
materials, so we don't have much in the way of metal ions in the stream.
The pumps are stainless.

Dennis

734.647.2055 Ofc

"People can be divided into 3 groups - those that make things happen, those
that watch things happen, and those that wonder what happened."  Within
which group do you belong?

On Tue, Sep 15, 2015 at 2:16 AM, Anteney I.M. <I.M.Anteney at soton.ac.uk>
wrote:

> Denis,
>
> I'm particularly interested in your comment about polishing the loops to
> get 1 mega-ohm resistance as we have struggled to do this especially when
> we dose the system with biocide and corrosion inhibitors. What are you
> using to polish the system, what inhibitors/biocides do you use and how do
> these affect the conductivity.
>
> Regards
>
> Iain
>
> Cleanroom Manager
> University of Southampton
>
> Sent from my iPhone
>
> On 15 Sep 2015, at 00:36, Dennis Schweiger <schweig at umich.edu<mailto:
> schweig at umich.edu>> wrote:
>
> Vito,
>
> here at UofMichigan, one of our PCW systems runs about 62.5F (16.9C) with
> a daily deviation of about 1F. The second runs about 59-60F (15C).  It too
> has a daily deviation of about 1F.  For both systems we may see a seasonal
> deviation of 3-4F as the main chiller plant transitions from "free cooling"
> to the use of chillers to create cooling water for the campus wide loop.
> We also "polish" both loops to 1 meg-ohm so that we have a "high
> resistance" in the RF cooling circuits.
>
> Dennis Schweiger
> University of Mighigan/LNF
>
> 734.647.2055 Ofc
>
> On Fri, Sep 11, 2015 at 3:47 PM, Vito Logiudice <
> vito.logiudice at uwaterloo.ca<mailto:vito.logiudice at uwaterloo.ca>> wrote:
> Dear Colleagues,
>
> The process chilled water loop in our cleanroom has consistently
> oscillated between ~15.4C and ~17.2C over a span of roughly 10 minutes. Our
> Plant Operations group is looking into the possibility of tightening this
> up for us by tuning the control sequence. They have asked for guidance on
> an acceptable specification.
>
> In light of this I would appreciate hearing from you as to your facility’s
> PCW temperature target and tolerance. Thank you much.
>
> Best regards,
> Vito
> --
> Vito Logiudice  P.Eng.
> Director of Operations, Quantum NanoFab
> University of Waterloo
> Lazaridis QNC 1207
> 200 University Avenue West
> Waterloo, ON           Canada N2L 3G1
> Tel.: (519) 888-4567  ext.
> 38703<tel:%28519%29%20888-4567%20%C2%A0ext.%2038703>
> Email: vito.logiudice at uwaterloo.ca<mailto:vito.logiudice at uwaterloo.ca>
> Website: https://fab.qnc.uwaterloo.ca
>
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu<mailto:labnetwork at mtl.mit.edu>
> https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
>
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu<mailto:labnetwork at mtl.mit.edu>
> https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20150915/be8505aa/attachment.html>


More information about the labnetwork mailing list