[labnetwork] Bulkhead between cleanroom and regular service room
Paolini, Steven
spaolini at cns.fas.harvard.edu
Fri Nov 8 17:56:32 EST 2019
Lei,
I need to know a few things before answering; Is your clean room a ballroom style with raised floors or is it a traditional "sidewinder" style where the return air passes into the chases and back up to the pre-filters?
Steve Paolini
Principal Equipment Engineer
Harvard University Center for Nanoscale Systems
11 Oxford St.
Cambridge, MA 02138
617- 496- 9816
spaolini at cns.fas.harvard.edu
www.cns.fas.harvard.edu
From: labnetwork-bounces at mtl.mit.edu <labnetwork-bounces at mtl.mit.edu> On Behalf Of Wang, Lei
Sent: Friday, November 08, 2019 2:20 PM
To: labnetwork at mtl.mit.edu
Subject: [labnetwork] Bulkhead between cleanroom and regular service room
Dear Colleagues,
We are working on cleanroom expansion, but might with a regular service room. Does anyone have experience with bulkhead method between cleanroom and 'dirty' service room?
The front of our new e beam evaporator will sit in cleanroom, but the back might be in a regular service room. Anyone knows is there any issue for this wall mount method? Do we need to seal all the gaps to avoid the contamination coming from the service room? Is the vibration a big problem when the system is running?
All suggestions and comments are welcome.
Thank you so much.
Lei
Lei Wang, Ph.D.
Yale West Campus Cleanroom
750 West Campus Drive
West Haven, CT, 06516
lei.z.wang at yale.edu<mailto:lei.z.wang at yale.edu>
203-737-6579
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20191108/8a809747/attachment.html>
More information about the labnetwork
mailing list