[labnetwork] High footfall in the cleanroom
Iulian Codreanu
codreanu at udel.edu
Fri Dec 22 09:04:46 EST 2023
Hi Savitha,
I would start by recalling where the maximum capacity of 50 came from.
If it was determined based on a code (fire, building) you have to stick
to it and look into strategies to spread out the work in the cleanroom.
If it was not based on a code, I think you have flexibility in allowing
70 users in at a given time if they do not "bump into each other".
Cheers,
Iulian
iulian Codreanu, Ph.D.
Director, Nanofabrication Facility
University of Delaware
Harker ISE Lab, Room 163
221 Academy Street
Newark, DE 19716
302-831-2784
https://udnf.udel.edu
On 12/22/2023 3:57 AM, Savitha P wrote:
>
> Hi!
>
> We are experiencing a high number of people in our cleanroom, with
> 50-70 users at a time against a maximum capacity of 50. I would
> appreciate it if you could share strategies used in your facilities to
> reduce the number of people in the cleanroom. Do you have any
> restrictions on students during the day or any incentives for working
> after office hours, for both startups and industry?
>
> Thanks,
> Savitha
>
> Dr. Savitha P
> Chief Operating Officer
> National Nanofabrication Centre
> Centre for Nanoscience and Engineering
> Indian Institute of Science
> Bangalore - 560012
> India.
> Ph. +91 80 2293 3319
> www.cense.iisc.ac.in
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
> https://mtl.mit.edu/mailman/listinfo.cgi/labnetwork