The silane bunker at Harvard is below grade, adjacent to a loading dock (building commissioned in 2007). It’s on a level of the building that’s adjacent to the loading dock (which itself is underground, accessed via ramp directly from the street). I recall that it’s on a mezzanine level of the nano complex and there was clever massing of the building that enabled siting of the bunker one level below grade. I was not privy to details before construction, involved in permitting or working with the AHJ.
> On Dec 7, 2017, at 9:19 PM, John D Shott <shott at stanford.edu> wrote:
>
> Mike:
>
> The institution for whom I used to work had a below-grade gas bunker in 1985 … when that was still legal.
>
> In 1995, we constructed two at-grade bunkers: one for toxics, flammable, and pyrophorics and one for corrosives.
>
> The one in which the silane lives has very heavily reverted walls, blast resistant doors, and a flimsy louvered ceiling … with no occupied spaces above or adjacent.
>
> Our AHJ would NEVER, EVER want us to have silane below grade. Despite my status as a leather-helmeted old fart, neither would I.
>
> There are likely online photos of silane "releases" that are quite persuasive.
>
> Good luck,
>
> John
>
> Sent from my iPhone
>
> On Dec 7, 2017, at 1:03 PM, Michael Hume <michael.hume at ualberta.ca <mailto:michael.hume at ualberta.ca>> wrote:
>
>> Hello Colleagues,
>>
>> We are in the process if installing a new PECVD system which will use 100% SiH4. In reviewing CGA-G13, it states:
>>
>> 7.2 Indoor storage and use
>> Buildings, rooms, or areas used for silane storage shall be constructed in accordance with the requirements of the local AHJ. Silane shall not be stored in locations below grade and silane bulk sources shall not be located indoors. For transfilling exceptions, see Section 18.
>>
>> In our case, an installation below grade may be preferred. I am wondering if anyone can provide any insight into the reasoning behind this. Does anybody store/use Silane below grade?
>>
>> Thank-you,
>> -Mike.
>>
>> --
>> PLEASE NOTE MY PHONE NUMBER HAS CHANGED:
>> 780-953-5081
>>
>>
>> Michael Hume
>> Operations Manager
>> University of Alberta - nanoFAB
>> W1-060 ECERF Building
>> 9107 - 116 Street
>> Edmonton, Alberta
>> Canada T6G 2V4
>> www.nanofab.ualberta.ca <http://www.nanofab.ualberta.ca/>
>> Ph:
>> 780-953-5081* (New)
>> _______________________________________________
>> labnetwork mailing list
>> labnetwork at mtl.mit.edu <mailto:labnetwork at mtl.mit.edu>
>> https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork <https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
> https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20171208/7297362a/attachment.html>
More information about the labnetwork
mailing list